    Temporary Network Issue - Charlotte Datacenter

    Hello,

    We are having temporary network issue at Charlotte datacenter, noc guys are working on it.
    Thanks for your patience.

    --------
    At 12:41 a utility fault caused phase B of the main power feed of DC3 to disconnect which caused our ATS to transfer power to our generator until which time we were on our generator ’til 1:15. Our ATS read a fault and and went into EPO with respect to the initial issue which caused phase B to fail. Local service technicians are working on solving the problem as fast as possible.
    -------
    Last edited by Sam; 03-06-2009 at 07:42 PM.
    Sam
    Ahosting, INC
    Reseller Hosting

  2. Sam
    Sam is offline Administrator
    Join Date
    May 2004
    Posts
    130

    Update
    ---------
    March 06, 2009 - 18h01
    Power circuits are now being brought up individually. During this process, some of you will find your services come up before others. Please be patient as you have been. Services are returning.
    --------
    Sam
    Ahosting, INC
    Reseller Hosting

  3. Sam
    Sam is offline Administrator
    Join Date
    May 2004
    Posts
    130

    Hello,

    The issue is over now.
    We do apologize for inconvience caused to you.
    Sam
    Ahosting, INC
    Reseller Hosting

  4. Sam
    Sam is offline Administrator
    Join Date
    May 2004
    Posts
    130

    March 07, 2009 03h15 a.m.

    Charlotte Datacenter is having network issue again and technicians are working on it.
    Sam
    Ahosting, INC
    Reseller Hosting

  5. Matt's Avatar
    Matt is offline Administrator
    Join Date
    May 2004
    Posts
    35

    March 7th, 2009

    As yet another unfortunate turn of events, the temporary generator we were using to supply power to DC3 caught fire at approximately 03:00 EST this morning. As a result of the fire we were forced to EPO DC3 by order of the Mecklenburg County Fire Marshall.

    Shortly after the fire began we requested a “replacement, replacement” generator from our vendor knowing the likely outcome of these events. Once the fire department had completely put out the fire it was determined that the generator was all but a complete loss and was of no further use to us.

    Due to delays outside of our control it took roughly four more hours for the “replacement, replacement” generator to be on site and we had it connected and supplying power in just under 30 minutes.

    At this time all service should be restored and we’re vigilantly monitoring the situation to ensure there are no further interruptions.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts